SEC1000: Inconsistent Load and Meter curves on SEMS
With the following instructions, you can check the Load and Meter curves on SEMS of your PV System equipped with a SEC1000.
In case of an error installation of the SEC1000, you may observe the load and meter curve inconsistent on SEMS. See the figure 1 and figure 2 as an examples of installation errors.
To monitor and visualize properly the SEC1000, please check and confirm the following points:
  1. Confirm the correct installation of the Current Transformers (CT).
  1. Confirm the correct ratio setup on the SEC1000.
  1. Checking the displayed real time data on Promate as follow:
  • Turn OFF the PV system
  • The energy consumed is supplied by the grid (import)
  • Refresh “Get Data” in Promate
  • RealTime Data” window will be displayed
  • Check the power values shown
  • Power (+): energy-to-grid export à impossible scenario (system OFF)
  • Check the installation (direction) of CTs
  • Power (-): importing power from the grid à correct
  • Check the consistency of the displayed values*
  • Check the “CT ratio” of the installed transformer (observe 2)
  • Check the correlation between the measured phase (voltage) and its CT
Please, carefully check the above points to monitor properly the Load and Meter curves on SEMS. Below, see the figure 3 as an example of the correct curves monitored by a SEC1000.
Please let me know if you need further support on this topic.
Best regards,
GoodWe
    • Related Articles
    • Change account for SEMS
      You indicated that you want to change your e-mail address to which you receive your notifications from the SEMSPortal.  To change your e-mail address in the SEMS Portal, you need to log in to www.semsportal.com with your old login credentials. After ...
    • Transfer the SEMSPortal-account to a new owner
      If there is a new owner of the inverter and you wish to transfer the monitor account on SEMS Portal. There are 2 ways to transfer the monitoring account to a new owner or email: Option 1 (Transfer your account and the historical data) This option ...
    • Adjusting the price per kWh in the SEMS Portal
      You indicated that you want to change the price per kWh in your monitoring environment.   The price per kWh is used to calculate your income from the PV system and is displayed in the SEMS Portal. Usually, the price per kWh is set up during the ...
    • PV Master Modes Explained
      There are 3 kinds of Work modes available in the PV Master app: General Mode Back-up mode Economical mode     General Mode The General Mode is the standard mode and is recommended in most situations. During this mode, self-consumption of the PV is ...
    • RCR – Ripple Controle Receiver
      Grid providers in some Markets (e.g. Germany for PV Systems >25kW or as requirement for state subsidies) require that PV Plants are controllable by them via RCR. Technically this is a small box with 4 Relays triggered by a simple form of PLC signal ...